Author Message
 Post subject: Preheating steam locomotive boilers to conserve service days
PostPosted: Wed Mar 16, 2022 3:16 pm 

Joined: Wed Oct 12, 2005 10:39 pm
Posts: 25
We have been using a stationary boiler to preheat our locomotive boilers by bubbling steam through a pipe just above the mud ring. We have been able to raise steam up to 90# on house steam. Because there is no fire in the firebox it doesn't count as a service day. My question is; if one didn't have a stationary boiler for steam how could one prewarm the boiler without house steam to save conserve service days and reduce thermal stress on the boiler? Like a lot of tourist railroads we have a two a week schedule so it doesn't make sense to keep a fire in it all the time. Is anyone else doing anything like this?


Offline
 Profile  
 
 Post subject: Re: Preheating steam locomotive boilers to conserve service
PostPosted: Wed Mar 16, 2022 3:58 pm 

Joined: Wed Mar 27, 2013 3:55 am
Posts: 173
Yes, the rack railroads in Austria and Switzerland!

https://dlm-ag.ch/wp-content/uploads/2020/06/Vorheiz-und-Vorw%C3%A4rmger%C3%A4te_d_e_2020-04-20.pdf

Mike


Offline
 Profile  
 
 Post subject: Re: Preheating steam locomotive boilers to conserve service
PostPosted: Wed Mar 16, 2022 4:54 pm 

Joined: Thu May 24, 2012 1:37 pm
Posts: 2492
Swiss rebuilt 8055 carries this a step further. That boiler and firebox is heavily lagged, with high-R-value damper panels, and they found it possible to use about 35kW of 'electric water heater elements' not only to keep the locomotive warm over cold winter weekends but to maintain steam pressure -- meaning there are no differential pressure cycles as well as no thermal cycling. Modern nanoinsulation systems could accomplish a similar result...

If you used a Cunningham circulator, you could probably put a chamber with throttling heating elements in the line between the downcoming port in the convection section and the manifold at the water leg, and run a circulating pump a bit like sous vide to maintain desired temperature (or start heating from cold).

I am in too much discomfort to check CFR on a phone, but I believe there is part of the service-day determination that involves pressure above atmospheric due to heating the boiler. That would limit the ability to heat the boiler above 212F, but I think it would make sense to keep the thing "as hot as possible" even if you used nitrogen blanketing or a similar idea to keep air out of the system...

_________________
R.M.Ellsworth


Offline
 Profile  
 
 Post subject: Re: Preheating steam locomotive boilers to conserve service
PostPosted: Wed Mar 16, 2022 4:58 pm 

Joined: Thu May 24, 2012 1:37 pm
Posts: 2492
Swiss rebuilt 8055 carries this a step further. That boiler and firebox are heavily lagged, with high-R-value damper panels, and they found it possible to use about 35kW of 'electric water heater elements' not only to keep the locomotive warm over cold winter weekends but to maintain steam pressure -- meaning there are no differential pressure cycles as well as no thermal cycling. Modern nanoinsulation systems could accomplish a similar result...

If you used a Cunningham circulator, you could probably put a chamber with throttling heating elements in the line between the downcoming port in the convection section and the manifold at the water leg, and run a circulating pump a bit like sous vide to maintain desired temperature (or start heating from cold).

_________________
R.M.Ellsworth


Offline
 Profile  
 
 Post subject: Re: Preheating steam locomotive boilers to conserve service
PostPosted: Wed Mar 16, 2022 6:38 pm 

Joined: Tue Sep 14, 2004 7:52 am
Posts: 2477
.


Last edited by Kelly Anderson on Mon Aug 26, 2024 5:46 pm, edited 1 time in total.

Offline
 Profile  
 
 Post subject: Re: Preheating steam locomotive boilers to conserve service
PostPosted: Wed Mar 16, 2022 7:19 pm 

Joined: Thu Sep 22, 2011 4:29 pm
Posts: 1899
Location: Youngstown, OH
I have been thinking of installing the equivalent of a home hot water heating system to keep 58 warm between runs. There would be a propane fired "boiler" and a low power draw circulating pump. The good thing about this setup is how common they are, meaning repair parts would be readily available. I would want to keep the temperature around 200 degrees which would start giving us steam pressure within about 15 minutes of starting the fire.

_________________
From the desk of Rick Rowlands
inside Conrail caboose 21747


Offline
 Profile  
 
 Post subject: Re: Preheating steam locomotive boilers to conserve service
PostPosted: Wed Mar 16, 2022 11:45 pm 

Joined: Fri Nov 07, 2008 11:21 am
Posts: 490
Why not simply use a gas or electric water heater commonly available at the hardware supply house? Connect the water column drain to the water heater intake, and connect the water heater output to the blowdown, all with quick fittings.

I agree with Rick Rowland's post.


Offline
 Profile  
 
 Post subject: Re: Preheating steam locomotive boilers to conserve service
PostPosted: Thu Mar 17, 2022 6:51 am 

Joined: Tue Jun 22, 2010 4:22 pm
Posts: 495
Mark Jordan wrote:
Why not simply use a gas or electric water heater commonly available at the hardware supply...


Bob Krieger could give you the details, but for awhile they used one of the huge water heaters made for car washes.

Speaking of preheating, a solar water heater might do well...aka a long length of black hose laid up in back and forth folds over your dark-colored roof, most effective in already-hot weather but surprisingly usable in many climates most of the year. It sounds funny, but it can save a lot of fuel by supplying the tank with water that is already very warm to hot. If you’ve even used a camp shower bag, either in a spot without running water or during long outages, you’ll know what I mean.

_________________
--Becky


Offline
 Profile  
 
 Post subject: Re: Preheating steam locomotive boilers to conserve service
PostPosted: Thu Mar 17, 2022 8:54 am 

Joined: Mon Aug 23, 2004 5:10 pm
Posts: 1182
In the early 1970's, Dan Ranger devised a layover system he used on Graham County Railroad Shay No. 1925. It consisted of a typical 50 gallon electric hot water heater that was connected to the locomotive by two hoses and depended solely on convection to circulate hot water through the boiler. This worked well on the engine, which was stored outside. He had a similar system on the GCRR's 70-ton GE.

In the 1980's. a railroad I worked for used hot water heater elements and hot tub pumps to keep EMD SW-style diesels warm, even down to in just above zero temperatures. The elements were enclosed in a section of 6 inch steel pipe.


Offline
 Profile  
 
 Post subject: Re: Preheating steam locomotive boilers to conserve service
PostPosted: Thu Mar 17, 2022 9:24 am 

Joined: Sun Aug 22, 2004 7:19 am
Posts: 6464
Location: southeastern USA
Consider strongly the location of the heater relative to the height of the boiler. The preheat / maintenance system built at Golden Spike drained the boilers unintentionally into the heaters down in the pit.......

_________________
“God, the beautiful racket of it all: the sighing and hissing, the rattle and clack of the cars over the rails. These were the sounds that made America the greatest country on earth." Jonathan Evison


Offline
 Profile  
 
 Post subject: Re: Preheating steam locomotive boilers to conserve service
PostPosted: Thu Mar 17, 2022 10:00 am 

Joined: Fri Nov 16, 2007 10:21 pm
Posts: 178
At Grand Canyon Railway, we devised a boiler preheater using a hot water heater that we recycled from a glycol heating system from a passenger car.

The heater runs off of 480V. We attached a circulating pump to it and fastened the whole thing to a 2 wheel 'dolly' for easy movement around the shop. Water is taken from the blowdown and enters the injector delivery pipe through a valve and pipe fitting we attached. That way the water follows normal circulation patterns - in through the boiler check on the front, out through the blowdown on the back.

The heater can bring the temperature up about 2 degrees an hour on a 4000 gallon boiler. We start 2 or 3 days before fire-up so that the water is just below boiling point when we light the fire. A thermostat on the heater allows us to control the temperature of the output water.

In theory, we could use this system to develop some amount of steam pressure. Once I came in on a weekend while the system was running, and the thermostat was a little too high. Apparently the water was boiling in the heater and creating steam bubbles, which were causing the boiler check to jump around and make a huge racket. To save wear on the boiler check, we stop around 195 degrees.

Works good to heat the water for hydro's too.

And as for the regulations in Part 230, A service day requires BOTH a fire in the firebox and pressure above atmospheric. So a water heater raising the pressure above 0 is not a service day, but a propane heater in the firebox is.

Eric


Offline
 Profile  
 
 Post subject: Re: Preheating steam locomotive boilers to conserve service
PostPosted: Thu Mar 17, 2022 2:04 pm 

Joined: Mon Mar 01, 2021 10:03 pm
Posts: 94
Location: Southeast PA
Kelly Anderson wrote:
I had set up a portable burner for use on SRC's locomotives that we used for a number of years.


Kelly, it sounds like this is past tense i.e. SRC no longer uses it. Did they upgrade to something newer or do away with it all together?

If SRC got rid of it all together, what was the reasoning behind that?


Offline
 Profile  
 
 Post subject: Re: Preheating steam locomotive boilers to conserve service
PostPosted: Thu Mar 17, 2022 3:01 pm 

Joined: Tue Sep 14, 2004 7:52 am
Posts: 2477
.


Last edited by Kelly Anderson on Mon Aug 26, 2024 5:45 pm, edited 1 time in total.

Offline
 Profile  
 
 Post subject: Re: Preheating steam locomotive boilers to conserve service
PostPosted: Fri Mar 18, 2022 11:23 pm 

Joined: Thu Sep 22, 2011 4:29 pm
Posts: 1899
Location: Youngstown, OH
Bought a used tankless water heater today. Working on the install. Should be an interesting project.

_________________
From the desk of Rick Rowlands
inside Conrail caboose 21747


Offline
 Profile  
 
 Post subject: Re: Preheating steam locomotive boilers to conserve service
PostPosted: Mon Mar 21, 2022 6:49 pm 

Joined: Thu Mar 24, 2011 12:07 pm
Posts: 1202
Location: Leicester, MA.
So fair question here, but with most locomotives what type of boiler could you use that would cover the water pre-heating that isn't going to cost through the nose? When I look at something like J&L 58, the boiler that pops into my head as an option is one of the larger Buderus boilers that we deal with through work. But even if you just keep the boiler water at what, 180 degrees? You're still going to have the question of oxygen in the environment. What would that do to your preheating unit to help account for that? Oxygen equals corrosion, and corrosion eventually leads to any boiler failing. Could you somehow coat the interior of the preheat unit with something like the apexerior that I know is used in locomotive boilers? And if I'm getting the name wrong, my apologies. Whatever it is that the Valley has used on their locomotive boilers.

_________________
Dylan M. Lambert
https://www.facebook.com/LambertLocomotive/


Offline
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 31 posts ]  Go to page 1, 2, 3  Next

All times are UTC - 5 hours [ DST ]


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to: