PostPosted: Wed Apr 26, 2023 11:19 pm 

Joined: Fri Dec 22, 2006 12:44 pm
Posts: 51
Location: Cheyenne, WY
Hello All,

Just a point of interest, please....................

When using ultrasonic thickness testing machines for measuring boiler plate to support a 1,472 day inspection, what criteria, procedures, practices, etc. are used to conduct the examination ?

Thank you.

Respectfully,

Dave Griner


Offline
 Profile  
 
 Post subject: Re: Ultrasonic Examination
PostPosted: Thu Apr 27, 2023 1:37 am 

Joined: Fri Nov 07, 2008 11:21 am
Posts: 490
One of the things that I see several folks make a mistake on is firebox sheets. I see the UT reading taken between staybolts. The UT reading should be taken immediately adjacent to the staybolt head, as close as possible with the transducer. The area around the stays will corrode due to stress corrosion cracking, and may be much thinner than the sheet between the stays. Here is a photo of a cross section of a crown sheet and staybolt taken out of a traction engine, which was operating at 150psi until a leak was noticed.


Attachments:
staybolt web.jpg
staybolt web.jpg [ 62.58 KiB | Viewed 7454 times ]
Offline
 Profile  
 
 Post subject: Re: Ultrasonic Examination
PostPosted: Thu Apr 27, 2023 8:08 am 

Joined: Sun Aug 22, 2004 7:19 am
Posts: 6464
Location: southeastern USA
Bottom of firebox just above mud ring. Boiler barrel at water line. Bottom of front tube sheet. Anywhere things were hung on the exterior of the boiler, you'll probably see the rust pit patches. Places around the firebox and barrel that are difficult to clean well during washouts...... all areas I've found trouble.

_________________
“God, the beautiful racket of it all: the sighing and hissing, the rattle and clack of the cars over the rails. These were the sounds that made America the greatest country on earth." Jonathan Evison


Offline
 Profile  
 
 Post subject: Re: Ultrasonic Examination
PostPosted: Sat Apr 29, 2023 1:06 pm 

Joined: Thu May 24, 2012 1:37 pm
Posts: 2492
Kelly, if you have the time, can you walk him through how to set up and execute a proper 'death ray' analysis?

_________________
R.M.Ellsworth


Offline
 Profile  
 
 Post subject: Re: Ultrasonic Examination
PostPosted: Sat Apr 29, 2023 4:15 pm 

Joined: Tue Sep 14, 2004 7:52 am
Posts: 2477
.


Last edited by Kelly Anderson on Tue Aug 20, 2024 7:07 pm, edited 1 time in total.

Offline
 Profile  
 
 Post subject: Re: Ultrasonic Examination
PostPosted: Sat Apr 29, 2023 4:53 pm 

Joined: Sun Sep 05, 2004 9:48 am
Posts: 1676
Location: Byers, Colorado
I figured that somebody who knows more than I do would step up on this one...

_________________
I am just an old man...
who wants to fix up an old locomotive.

Sammy King


Offline
 Profile  
 
 Post subject: Re: Ultrasonic Examination
PostPosted: Sat Apr 29, 2023 5:42 pm 

Joined: Sun Sep 05, 2004 9:48 am
Posts: 1676
Location: Byers, Colorado
Kelly Anderson wrote:
I expect that he was trying to initiate discussion, and I for one am pretty disappointed in the small number of responses.


Much as I hate to say this, the discussion board has slowed down considerably since the mods have (justifiably) tried to throttle down the trolling a few notches.

_________________
I am just an old man...
who wants to fix up an old locomotive.

Sammy King


Offline
 Profile  
 
 Post subject: Re: Ultrasonic Examination
PostPosted: Sat Apr 29, 2023 6:18 pm 

Joined: Thu Oct 08, 2015 11:54 am
Posts: 2055
Location: New Franklin, OH
I’m mostly a diesel guy so I have nothing to add but I find technical discussions on steam fascinating. Hope this thread picks up.

_________________
Eric Schlentner
Turner of Wrenches, Drawer of Things


Offline
 Profile  
 
 Post subject: Re: Ultrasonic Examination
PostPosted: Sat Apr 29, 2023 10:02 pm 

Joined: Wed Oct 25, 2006 12:12 pm
Posts: 213
Location: Bremerton, WA
The CFR requires inspection but doesn't tell you HOW to do it. Do you just want the numbers to equal the values which will pencil out well when calculating your Form 4 or do you want to know the truth? Nothing you prevents you from checking next to staybolts, just above the mudring, around blowdowns, or even arch tubes.
https://www.ecfr.gov/current/title-49/s ... I/part-230
It also requires the owner/operator to inspect tenders. Large shops had an entire department dedicated to maintenance and repair of tenders. Although I've never seen a tender come "unzipped", it could happen and it would never be at a convenient time or place. I've seen a lot of leaking slope sheets and weeping tanks though the years. 'T' iron and rods thin? Sides rotten at the bottom? Might want to use the UT while it's out of the box. Ever see a grid on a smokebox? You won't find much about them in NBIC or ASME documents because it's not part of the pressure vessel - but it is the only thing holding the pressure vessel to the rest of the locomotive. The owner/operator is responsible for a locomotive and tender which is safe and suitable for service. Lots of good reading here: https://www.govinfo.gov/content/pkg/GOV ... 1ee412.pdf

_________________
Locomotives are like Submarines; cylindrical, black, and use steam propulsion.


Offline
 Profile  
 
 Post subject: Re: Ultrasonic Examination
PostPosted: Sun Apr 30, 2023 12:06 pm 

Joined: Thu Jan 01, 2009 1:35 pm
Posts: 52
I’m with Kelly on this. Mr. Griner is someone I would consult if I had questions on the subject.
So I’ll add a question; does FRA require all tubes and flues to be removed at the 1472 day inspection, as I assumed, or is there an allowance for superheater flues to be left in and UT’d for thickness? I’ve recently heard some discussion of this.
Thanks.


Offline
 Profile  
 
 Post subject: Re: Ultrasonic Examination
PostPosted: Sun Apr 30, 2023 1:24 pm 

Joined: Tue Aug 31, 2004 10:38 pm
Posts: 84
Adam Phillips wrote:
The CFR requires inspection but doesn't tell you HOW to do it. Do you just want the numbers to equal the values which will pencil out well when calculating your Form 4 or do you want to know the truth? Nothing you prevents you from checking next to staybolts, just above the mudring, around blowdowns, or even arch tubes.
https://www.ecfr.gov/current/title-49/s ... I/part-230
It also requires the owner/operator to inspect tenders. Large shops had an entire department dedicated to maintenance and repair of tenders. Although I've never seen a tender come "unzipped", it could happen and it would never be at a convenient time or place. I've seen a lot of leaking slope sheets and weeping tanks though the years. 'T' iron and rods thin? Sides rotten at the bottom? Might want to use the UT while it's out of the box. Ever see a grid on a smokebox? You won't find much about them in NBIC or ASME documents because it's not part of the pressure vessel - but it is the only thing holding the pressure vessel to the rest of the locomotive. The owner/operator is responsible for a locomotive and tender which is safe and suitable for service. Lots of good reading here: https://www.govinfo.gov/content/pkg/GOV ... 1ee412.pdf



Per part 230.31(b), as long as you can enter the boiler to thoroughly clean and inspect the interior and it can be proven that the flues are safe and suitable for service using an appropriate NDE testing method, then the superheater flues do not need to be removed. However, they do have to be removed if the FRA inspector or owner/operator considers it necessary due to identifiable safety concerns.

How many operations have been able to utilize this exception?

Ed


Offline
 Profile  
 
 Post subject: Re: Ultrasonic Examination
PostPosted: Sun Apr 30, 2023 2:37 pm 

Joined: Tue Sep 14, 2004 7:52 am
Posts: 2477
.


Last edited by Kelly Anderson on Tue Aug 20, 2024 7:06 pm, edited 1 time in total.

Offline
 Profile  
 
 Post subject: Re: Ultrasonic Examination
PostPosted: Sun Apr 30, 2023 2:41 pm 

Joined: Thu May 24, 2012 1:37 pm
Posts: 2492
I don't think Dave Griner would be asking at all if he weren't interested in other people's 'detail design' and methodology for this kind of NDT.

I have no experience in it other than from the armchair, so have nothing of any practical value to contribute.

_________________
R.M.Ellsworth


Offline
 Profile  
 
 Post subject: Re: Ultrasonic Examination
PostPosted: Sun Apr 30, 2023 3:07 pm 

Joined: Wed Oct 25, 2006 12:12 pm
Posts: 213
Location: Bremerton, WA
"I would advise going with the truth, no matter how much more it costs."

Exactly! It's the right thing to do and nobody wins when something bad happens whether it is due to ignorance or willful noncompliance.

_________________
Locomotives are like Submarines; cylindrical, black, and use steam propulsion.


Offline
 Profile  
 
 Post subject: Re: Ultrasonic Examination
PostPosted: Sun Apr 30, 2023 7:54 pm 

Joined: Mon Aug 23, 2004 10:49 am
Posts: 773
I've personally never done an ultrasound, but learning the right way to do it is what I am interested in.


Offline
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 26 posts ]  Go to page 1, 2  Next

All times are UTC - 5 hours [ DST ]


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to: